Wiring ?

Meant to imply safer to replace just the motor to a 110v. Plus if the motor isn't replaced with a 110v it's likely the compressor will fail due to insufficient amperage using a step up converter and rewiring the garage all the way to the circuit breaker with heavier gauge wire since its conversion is gonna have a notable power loss and draw at least double the current.

It's a 4500psi compressor and the draw is more than home shop power tools.
 

  • Will the 220v europe model work with 230v in usa?
  • benjamin from USA asked:
    Hi, i am interested in purchasing compressor for traveling. What is the frequency of that compressor? I will need 220V and 60HZ. Cheers Benjamin.

I think you would have to find a 120v 60hz motor rated for the load?
 
The answer to your question will be on the motor nameplate for example it may say 120/240 if it can be wired for dual voltages. If the nameplate only has one voltage rating. Its not doable also remember to look at your full load amperage. If it draws say 10 amps. wired for 240 if the wiring allows 120 it will draw double amperage so 20 amps as per example. Your house receptacle and wiring are protected from overcurrent by the breaker usually in a common house breaker either a 15 or 20 amp circuit. Drawing excessive amperage will cause the breaker to trip. Replacing the breaker to a larger breaker is not the answer as the wiring and receptacle will burn up. Thats about as simple an answer I could type. I don't know what the motor is rated without researching it.